1. Obtain a VOM and locate the Goodman Split System 2. Set up the VOM to read continuity. (Ohm's) 3. During the first part of
1. Obtain a VOM and locate the Goodman Split System 2. Set up the VOM to read continuity. (Ohm's) 3. During the first part of this exercise you will be checking to see if each winding in the compressor is good. 4. Ensure power to the outdoor condensing unit is OFF and discharge all capacitors. If you have forgotten how to do this, let the staff know at once. 5. Disconnect the compressor wires from the compressor terminals. (Document wire locations) 6. Place one lead on the Start terminal and one lead on the Common Terminal Record the resistance of the Start Winding. ohms. Measure the resistance between the Run Terminal and the Common Terminal. Record the resistance of the Run Winding. ohms. Measure the resistance between the Start and Run terminals. Record the resistance through the motor windings. ohms. 7 .Now check to see if the Compressor is grounded. Set up the meter to read Ohm's. Hold one lead on one of the copper lines attached to the compressor. Use the other lead to go to each of the compressor terminals Record the results. Common to Ground Start to Ground Run to Ground Explain the measurements and the condition