A 3ph 100 MVA 3.3/66 kV transformer T1 is connected to two buses of voltages respectively 3.3 kV and 66 kV. The fault MVA at

A 3ph 100 MVA 3.3/66 kV transformer T1 is connected to two buses of voltages respectively 3.3 kV and 66 kV. The fault MVA at 66 kV bus is 1000 MVA. Calculate the fault MVA at 3.3 kV bus. Answer : Faut MVA = 14285 MVA