A new electricity transmission line is planned to supply an outlying area and two different conductor sizes are being considered. The capital cost of the

A new electricity transmission line is planned to supply an outlying area and two different conductor sizes are being considered. The capital cost of the line is estimated at $15,600,000 for conductor A and $18,700,000 for conductor B. The energy losses in the line in the first year are estimated at $146,000 for conductor A and $75,000 for conductor B. If conductor A is used the load capacity of the line will be reached in 13 years. The line will then need to be upgraded by replacing conductor A with conductor B at a present day cost of $5,700,000.

The estimated inflation rate for the costs involved is 2% p.a. The company borrows funds at an interest rate of 5% p.a.

(The cost of energy will decrease because of increased renewable energy in the system, but the actual losses will increase because of the increased electrical load. For the purpose of this question, assume that these two effects can be ignored because they cancel each other out.)

Which conductor should be used?

The effective discount rate should be used where appropriate: image text in transcribed

Step by Step Solution

There are 3 Steps involved in it

Step: 1

blur-text-image

Get Instant Access to Expert-Tailored Solutions

See step-by-step solutions with expert insights and AI powered tools for academic success

Step: 2

blur-text-image

Step: 3

blur-text-image

Ace Your Homework with AI

Get the answers you need in no time with our AI-driven, step-by-step assistance

Get Started

Recommended Textbook for

Quantitative Financial Risk Management

Authors: Constantin Zopounidis, Emilios Galariotis

1st Edition

1118738187, 978-1118738184

More Books

Students also viewed these Finance questions

Question

2. What potential barriers would you encourage Samuel to avoid?

Answered: 1 week ago