A refrigerator with Freon-12 as refrigerant operates with an evaporator temperature of 248 K (P = 1.2bar, S = 0.7130 kJ/kg-K, H = 176.22 kJ/kg)

A refrigerator with Freon-12 as refrigerant operates with an evaporator temperature of 248 K (P = 1.2bar, S = 0.7130 kJ/kg-K, H = 176.22 kJ/kg) and a condensation temperature of 298 K (P = 6.2 bar, S = 0.224 kJ/kg-K, H = 59.17 kJ/kg). The saturated liquid leaving the condenser is passed through an expansion valve and an evaporator. The vapor leaving evaporator is saturated.

c) The liquid leaving the condenser is passed through a counter current heat exchanger where it

gives off its heat to the vapor leaving the evaporator. The liquid leaving the condenser is at 298 K and the vapor leaving the evaporator is at 248 K. In the exchanger the vapor gets heated to 292 K (P = 1.2 bar, S = 0.8164 kJ/kg-K, H = 203.53 kJ/kg). What would be the circulation rate of Freon-12?

d) What is the COP in each of the above cases?

a) If the refrigerator is rated at 1.5 ton, what is the circulation rate of Freon-12?

b) By how much circulation rate would be reduced, if the throttle valve were replaced by a turbine?

Step by Step Solution

There are 3 Steps involved in it

Step: 1

blur-text-image

Get Instant Access to Expert-Tailored Solutions

See step-by-step solutions with expert insights and AI powered tools for academic success

Step: 2

blur-text-image_2

Step: 3

blur-text-image_3

Ace Your Homework with AI

Get the answers you need in no time with our AI-driven, step-by-step assistance

Get Started

Recommended Textbook for

Accounting Principles Volume 1

Authors: Jerry J. Weygandt, Donald E. Kieso, Paul D. Kimmel, Barbara Trenholm, Valerie Warren, Lori Novak

9th Canadian Edition

978-1119786818, 1119786819

More Books

Students also viewed these Accounting questions