An 18,000 Btu/h split air conditioner running at full load is used to keep a room at 22C in an environment at 33C. The power

An 18,000 Btu/h split air conditioner running at full load is used to keep a room at 22°C in an environment at 33°C. The power input to the compressor is 3.4 kW. 

Determine

(a) the rate of heat rejected in the condenser, in kJ/h, 

(b) the COP of the air conditioner, and 

(c) the rate of cooling, in Btu/h, if the air conditioner operates as a Carnot refrigerator for the same power input.

Step by Step Solution

3.41 Rating (154 Votes )

There are 3 Steps involved in it

Step: 1

Giren load to refrigerator Q 18000 Btuju data The cooling Pawer in put Win 34 kW ... blur-text-image

Get Instant Access to Expert-Tailored Solutions

See step-by-step solutions with expert insights and AI powered tools for academic success

Step: 2

blur-text-image

Step: 3

blur-text-image

Ace Your Homework with AI

Get the answers you need in no time with our AI-driven, step-by-step assistance

Get Started

Recommended Textbook for

Physics Principles with Applications

Authors: Douglas C. Giancoli

7th edition

978-0321869111, 321625927, 9780321733627, 321869117, 9780321625922, 321733622, 978-0321762429

More Books

Students also viewed these Mechanical Engineering questions

Question

Write down the Limitation of Beer - Lamberts law?

Answered: 1 week ago

Question

Discuss the Hawthorne experiments in detail

Answered: 1 week ago

Question

Explain the characteristics of a good system of control

Answered: 1 week ago

Question

State the importance of control

Answered: 1 week ago

Question

Write the binary number 1010101010101010 as a decimal number.

Answered: 1 week ago