Atmospheric air at 300C dry bulb temperature and 75% RH enters a cooling coil at 200m3/min. The coil dew point temperature is 140C and
Atmospheric air at 300C dry bulb temperature and 75% RH enters a cooling coil at 200m3/min. The coil dew point temperature is 140C and its bypass factor is 0.1. Determine (1) the Temperature of air leaving the coil, (ii) the Capacity of the cooling coil in tons of refrigeration, and (iii) the amount of water vapor removed per minute.
Step by Step Solution
★★★★★
3.41 Rating (151 Votes )
There are 3 Steps involved in it
Step: 1
SOLUTIONS To determine the temperature of air leaving the coil we need to consider the bypass factor and the cooling effect of the coil The bypass factor B is defined as the ratio of air that bypasses ...Get Instant Access to Expert-Tailored Solutions