Consider an existing 200 kW motor with 94% efficiency at a load factor of 0.9. The motor runs for 6000 hours per annum. Determine
Consider an existing 200 kW motor with 94% efficiency at a load factor of 0.9. The motor runs for 6000 hours per annum. Determine the payback period (simple undiscounted payback) if this motor is replaced with a 200 kW new motor with 96% efficiency assuming the new motor runs at same load factor and operating hours per annum. The energy costs are 8 cents/kWh. The cost of the new motor is $7,000.00. Student answer
Step by Step Solution
There are 3 Steps involved in it
Step: 1
To determine the payback period we need to calculate the annual savings and then divide it by the co...Get Instant Access to Expert-Tailored Solutions