Exercise 3 In the refrigerator laboratory of a testing institute, a climatic chamber is operated in water energy consumption measurements are carried out on refrigerators.

Exercise 3
In the refrigerator laboratory of a testing institute, a climatic chamber is operated in water
energy consumption measurements are carried out on refrigerators. In order to maintain the
conditions required for a so-called standard energy consumption measurement, a temperature
of N=25C and a relative humidity of N=60% must be kept constant at a height next
the appliances (see sketch). The climatic chamber is perfectly insulated except for the flow
through which a constant heat flux QFloor=200W escapes, since the climatic chamber
located in the basement and the floor has a temperature of Floor=20C. During a running
measurement, there are NKG=8 refrigerator cooling units in the chamber, each of which emit
an average heat flux of QKG=50W to the chamber air. The chamber air conditioning system
sucks in air to be conditioned near the floor, which has cooled to a temperature of 1=24
due to heat loss via the chamber floor. Of the intake air mass flow, 20% is replaced by free
air, which on a summer day has a temperature of F=30C and a relative humidity of F
70%. Subsequently, the mixed air is cooled in a heat exchanger by a tempered brine, with
temperature of Brine=10C. The water condensed out of the air during cooling is completly
separated. Subsequent to the dehumidification process a downstream heater finally brings the
air to the required inlet temperature of 4=22C supplying the heat flow QHeating.
1) Calculate the mass flow of dry air m1 so that
constante temperature condition are maintained in the
climatic chamber?
2) calculate the temperature 2 and relative humidity
Q2 after mixing the air steams?
3) calculate the temperature the air must be cooled
to be dehumidification?
4) calculate the heat flux Qwu absorbed by Brine
in the heat exchanger to cool the air down to
the dehumidification temperature 2 which
mas flow rate mw must be removed when
dehumidifyning the air?
5) catculate the heat flow of the heater QHeating
by which the air is bought to the inlet
temperature 4=22C after dehumidification Material data:
all changes of state of humid are performed
at p=1.01325 bar
specific isobaric heat capacities:
Cpair=1.004KJkg*K
Cp(water)Vapor=1,86KJkgK
Cp(water)Liquid=4,186KJKgK
Specific gas constants:
Rair=0.2871KJKgK,Rwater=0.46151KJKgK
Enthalpy of Vaporization of water at 0C=
hy=2500kJky
Vapor pressure curve of water:
ln(PP0)=12,41682-4222,037KT-31,95K
with T in K and P0=1 bar

Step by Step Solution

There are 3 Steps involved in it

Step: 1

blur-text-image

Get Instant Access to Expert-Tailored Solutions

See step-by-step solutions with expert insights and AI powered tools for academic success

Step: 2

blur-text-image

Step: 3

blur-text-image

Ace Your Homework with AI

Get the answers you need in no time with our AI-driven, step-by-step assistance

Get Started

Recommended Textbook for

Thermodynamics for Engineers

Authors: Kenneth A. Kroos, Merle C. Potter

1st edition

1133112862, 978-113311286

More Books

Students also viewed these Chemical Engineering questions

Question

List the steps in risk management planning.

Answered: 1 week ago