The sensitivity of a node to real power changes is 100 MW/kV of line voltage and that to reactive power changes is 10 MVAr/kV

  

The sensitivity of a node to real power changes is 100 MW/kV of line voltage and that to reactive power changes is 10 MVAr/kV of line voltage. (v) How much reactive compensation would have to be introduced at a point to maintain the voltage constant for a real power change of 55MW?

Step by Step Solution

3.37 Rating (153 Votes )

There are 3 Steps involved in it

Step: 1

Solution Real power change of Line voltage AP Reacti... blur-text-image