Moist air at 50F dry bulb and 40% relative humidity flows at 1840 cfm across a heating coil. The air is sensibly heated at a
Moist air at 50F dry bulb and 40% relative humidity flows at 1840 cfm across a heating coil. The air is sensibly heated at a rate of 13,200 Btu/h. What is the dry bulb temperature and relative humidity of the air leaving the heater?
The answer is (T = 56.5F, Twb = 43.4F)