Answered step by step
Verified Expert Solution
Link Copied!

Question

1 Approved Answer

Q4. In a building environmental performance assessment, credits are given for better daylight performance and reduction in energy use for air-conditioning. Assuming that daylight performance

Q4. In a building environmental performance assessment, credits are given for better daylight performance and reduction in energy use for air-conditioning.

Assuming that daylight performance is assessed by the window-to-wall ratio (r) and energy for an air-conditioned space is assessed by the percentage reduction in annual thermal energy consumption (TEC, kWh/m2 year). The credit scales for these two assessment criteria are given in Table Q4.1. Given also are the baseline and design parameters in Table Q4.2 for the environmental assessment.

Table Q4.1 Credit scale for the two assessment criteria (No interpolation; credits are in integer values)

R No. credit(s) % reduction in TEC No. of credit(s)
0.9 3 0
0.7 2 10 4
0.5 1 20 8
0 30 12
40 16
50 20

Table Q4.2 Summary of baseline and design parameters of the building

Parameter Baseline Design Parameter Baseline Design Additional capital cost HK$/m Additional maintenance cost HK$/m2
T 25 25 r 0.3 0.5 ? ?
A 1000 1000 U 40 34 6 / 1 1 / 1
V 4000 4000 S 0.8 0.6 4 / 0.1 0.25 / 0.1
L 40 40

image text in transcribed

(a) Determine the % reduction in the TEC of the air-conditioned space for the design, and hence the number of credits to be scored by the design. (4 marks)

You are given the equation below for prediction of annual thermal energy consumption E for the air-conditioning space in kW/myear, where I is indoor air temperature in C, A and V are area and volume of the floor in m and m respectively, r is window-to-wall ratio, L is the characteristic length in m, U is overall U-value in W/mK, and S is the shading coefficient. E=27749 7-0.88 A-0.79 70.22 0.39 0.37 0.36 50.49, where L=max(Width, Depth) of a floor plan. You are given the equation below for prediction of annual thermal energy consumption E for the air-conditioning space in kW/myear, where I is indoor air temperature in C, A and V are area and volume of the floor in m and m respectively, r is window-to-wall ratio, L is the characteristic length in m, U is overall U-value in W/mK, and S is the shading coefficient. E=27749 7-0.88 A-0.79 70.22 0.39 0.37 0.36 50.49, where L=max(Width, Depth) of a floor plan

Step by Step Solution

There are 3 Steps involved in it

Step: 1

blur-text-image

Get Instant Access to Expert-Tailored Solutions

See step-by-step solutions with expert insights and AI powered tools for academic success

Step: 2

blur-text-image

Step: 3

blur-text-image

Ace Your Homework with AI

Get the answers you need in no time with our AI-driven, step-by-step assistance

Get Started

Recommended Textbook for

Federal Tax Accounting 2022

Authors: Frank L. Brunetti

1st Edition

080805631X, 9780808056317

More Books

Students also viewed these Accounting questions

Question

Describe five career management practices

Answered: 1 week ago