Room sensible temperature load: 85.15 kW Room Latent heat load: 14.54 kW A retail shop located in a city at 30N latitude has the

 

Room sensible temperature load: 85.15 kW Room Latent heat load: 14.54 kW A retail shop located in a city at 30N latitude has the following loads. The summer outside and inside design conditions are: Outside: 40 C DB, 27C WB Inside: 25C DB, 50% RH 70 cmm of ventilation air is used. Determine the following: i. ii. iv. V. vi. Ventilation Load Grand total heat Effective sensible heat factor Apparatus dew point Dehumidified air quantity Condition of air entering and leaving apparatus Assume a suitable bypass factor of the cooling coil. Note: Use psychrometric chart.