Answered step by step
Verified Expert Solution
Link Copied!

Question

1 Approved Answer

Two systems are interconnected by two 16 MW tie lines. System A has four 30 MW generating units with forced outage rates of 10%. System

Two systems are interconnected by two 16 MW tie lines. System A has four 30 MW generating units with forced outage rates of 10%. System B has eight 15 MW generating units with forced outage rates of 8%. Calculate the expected loss of load in each system in days and in MW for a one-day period, given that the peak load in both System A and System B is 100MW, 

(a) if the tie lines are 100%reliable, 

(b) if the tie lines have failure rates of 5 failures/year and average repair times of 24 hours.

Step by Step Solution

3.40 Rating (150 Votes )

There are 3 Steps involved in it

Step: 1

blur-text-image

Get Instant Access to Expert-Tailored Solutions

See step-by-step solutions with expert insights and AI powered tools for academic success

Step: 2

blur-text-image

Step: 3

blur-text-image

Ace Your Homework with AI

Get the answers you need in no time with our AI-driven, step-by-step assistance

Get Started

Recommended Textbook for

Fundamentals of Thermodynamics

Authors: Richard E. Sonntag, Claus Borgnakke, Gordon J. Van Wylen

6th edition

471152323, 978-0471152323

More Books

Students also viewed these Electrical Engineering questions