Air flowing at the rate of 80m3/min at 35C dry bulb temperature and 50% relative humidity is mixed with another stream flowing at the rate
Air flowing at the rate of 80m3/min at 35C dry bulb temperature and 50% relative humidity is mixed with another stream flowing at the rate of 20m3/min at 21C dry bulb temperature and 50% relative humidity. The mixture flows over a cooling coil whose apparatus dew point temperature is 5C and by-pass factor is 0.2. Find dry bulb temperature and relative humidity of air leaving the coil. If this air is supplied to an airconditioned room where dry bulb temperature of 21C and relative humidity of 50% are maintained, and determine: a) Room sensible heat factor; and b) Cooling load capacity of the coil in tons of refrigeration