The connected load at 50Hz is 30000Mw in area 1 and 50000Mw in area 2. The load in each area varies 2% for every 1.5% change in frequency.
Area1 is importing 1500Mw from area 2. The speed regulation, R, is 4% for all units.
Area 1 is operating with a spinning reserve of 1500Mw spread uniformly over a generation of 5000Mw capacity, and area 2 is operating with spinning reserve of 2000Mw spread uniformly over a generation of 9000Mw.
If the loss of 1500Mw load in area 1, assuming that there are no supplementary controls. The tie line power is:
\table[[533.134Mw
image text in transcribed