12.5 a. Apply and set distance-type relays at Stations H and R for the protection of line HR in the system in Figure P12.5. Set

12.5 a. Apply and set distance-type relays at Stations H and R for the protection of line HR in the system in Figure P12.5. Set zone 1 units for 90% of the protected line, zone 2 to reach 50% into the next line section beyond the protected line, and zone 3 for 120% of the next line section. b. Plot this system on an RX diagram with the origin at bus H. Plot the relay settings of part 1 using mho-type characteristics. The mathematical formula for a circle through the origin or relay location is where Zs is the relay setting at 758:

image text in transcribed

The first term is the offset from the origin at 758 and the second term is the radius. This when f is 758, Z0, the relay location; when f is 2558, ZZs the forward reach.

c. What is the maximum load in MVA at 87% pf. that can be carried over line HR without the distance relays operating? Assume that the voltage transformer ratio RV1000 and the current transformer ratio Rc80.

image text in transcribed

Step by Step Solution

There are 3 Steps involved in it

Step: 1

blur-text-image

Get Instant Access to Expert-Tailored Solutions

See step-by-step solutions with expert insights and AI powered tools for academic success

Step: 2

blur-text-image

Step: 3

blur-text-image

Ace Your Homework with AI

Get the answers you need in no time with our AI-driven, step-by-step assistance

Get Started

Recommended Textbook for

Logics For Databases And Information Systems

Authors: Jan Chomicki ,Gunter Saake

1st Edition

1461375827, 978-1461375821

More Books

Students also viewed these Databases questions

Question

How is intelligence defined?

Answered: 1 week ago