Consider the simple feeder shown in Figure 1.1 with conductor data as in Table and consumption data as in the following tables. A second feeder
Consider the simple feeder shown in Figure 1.1 with conductor data as in Table and consumption data as in the following tables. A second feeder section (CE) is connected to point C, with 35mm2 conductor cross section. The minimum and maximum consumptions at point E are 900 and 500kW, respectively. Calculate the first and the second hosting capacity for the different feeder sections. A B D Feeder section AB BC CD Conductor size Ampacity Maximum permissible power 185 mm 388 A 10 MVA 95 mm2 268 A 7 MVA 35 mm 151 A 3.9 MVA B D Maximum active power Maximum reactive power Minimum active power Minimum reactive power 2 MW 1.3 Mvar 500 kW 300 kvar 3.5 MW 2 Mvar 900 kW 2.5 MW 1.3 Mvar 700 kW 500 kvar 500 kvar Pgen, max Pcons, min + P2 + Qzons, max dons, min Pgen, max