Question
a) With the aid of the design chart given , evaluate the settlement (in mm) of the above square footing under the influence of the
a) With the aid of the design chart given, evaluate the settlement (in mm) of the above square footing under the influence of the water table if the allowable bearing pressure (qallow) is given as 2,500 kN/m2.
Note that you have to convert the square footing to circular footing to use the design chart
b) If the immediate next column to this particular one settles 125.5 mm and the column spacing is 6.1 m, what is the angular distortion (dimensionless) of the building at this location?
You will need your previous answer from the question immediately above to work on this question.
c) Using the appropriate chart provided, how critical is the structural health of the building?
Note: Select only one answer
A) Visible cracks in brick in-fill panels
B) Level of overstress in diagonal members becomes significant
C) Structural damage to the building is expected
D) Damage to building frames observable
Figure 3 shows a square footing with B = 2.5m. The water table is deep enough to be ignored. The footing rests at depth, D = 1.5m from the ground surface. The dry unit weight and cohesion of the surrounding dense silty sand are 20kN/m and 10 kN/m, respectively. Use Terzaghi's method to solve this problem. D = 1.5m h = 4.0m qallow = 2500 kN/m B = 2.5m Dense silty sand Ydry = 20 kN/m Ysat 22 kN/m c' = 10 kN/m E = 50,000 kN/m v = 0.2 Bedrock Figure 3. Square footing on dense silty sand
Step by Step Solution
3.33 Rating (156 Votes )
There are 3 Steps involved in it
Step: 1
Get Instant Access to Expert-Tailored Solutions
See step-by-step solutions with expert insights and AI powered tools for academic success
Step: 2
Step: 3
Ace Your Homework with AI
Get the answers you need in no time with our AI-driven, step-by-step assistance
Get Started